it's for combustion air, and yes the room needs to either, be a certain size, or be connected via vents to a room that is big enough, or have a vent to outside to bring fresh air in (it may not have to be hooked up directly to the furnace)
Is the return air (see top image, lower right of furnace) venting to a large room good enough?
Or does the whole machine (i.e. where that "fresh air inlet" is) need to be in the "large" room?


My concern is back drafting, a natural draft flue is bad in a tight house. A power vent is better (which i think this system has, and direct vent is best.
I don't think it has a power vent. Unless this is something that only turns on when the heat is running?

Thanks for your input!

Offline CountValentine

  • Dansdeals Lifetime 10K Presidential Platinum Elite
  • *******
  • Join Date: Mar 2013
  • Posts: 17461
  • Total likes: 8280
  • DansDeals.com Hat Tips -1
  • Gender: Female
    • View Profile
  • Location: Poland - Exiled
  • Programs: DAOTYA, DDF Level 3, 5K Lounge
Re: HVAC (heating and AC) question
« Reply #421 on: May 21, 2024, 08:15:31 PM »
Where is the furnace located? How big is the room?
This has a whole section on ventilation.
https://resource.gemaire.com/is/content/Watscocom/Gemaire/rheem_r801ca_en_ii.pdf
« Last Edit: May 21, 2024, 08:19:20 PM by CountValentine »
Only on DDF does 24/6 mean 24/5/half/half
Simone Biles: “I love my black job”

Offline notyettaken

  • Dansdeals Gold Elite
  • ***
  • Join Date: Aug 2022
  • Posts: 184
  • Total likes: 228
  • DansDeals.com Hat Tips 2
    • View Profile
  • Location: home
Re: HVAC (heating and AC) question
« Reply #422 on: May 21, 2024, 09:59:39 PM »
Where is the furnace located? How big is the room?
This has a whole section on ventilation.
https://resource.gemaire.com/is/content/Watscocom/Gemaire/rheem_r801ca_en_ii.pdf
see page 14-16.
Is the return air (see top image, lower right of furnace) venting to a large room good enough?
the return air does not help because the combustion air intake does not connect to it.

Or does the whole machine (i.e. where that "fresh air inlet" is) need to be in the "large" room?
yes 50 cubic feet per 1000 btu
if it is in a smaller space the manual (page 14-16) says how big of a vent is needed to connect to a larger room.

I don't think it has a power vent. Unless this is something that only turns on when the heat is running?

yes only when heat is running.
however I'm not sure how much pressure the blower on this unit makes. so I would be concerned about it in a tight house, see page 15
Quote
If the confined space is within a building with tight construction,
combustion air must be taken from outdoors or from an area
freely communicating with the outdoors.

Offline Alexsei

  • Dansdeals Lifetime Presidential Platinum Elite
  • *********
  • Join Date: Sep 2011
  • Posts: 6296
  • Total likes: 2000
  • DansDeals.com Hat Tips 5
    • View Profile
    • Travel & Kivrei Zadikim
  • Location: Truckistan
  • Programs: COVID-24
Re: HVAC (heating and AC) question
« Reply #423 on: May 26, 2024, 03:28:52 PM »
My central AC unit covers main floor + basement, however my basement ends up being 4-5° cooler than the main floor, my playroom is so cold that kids turn on the baseboard heat there 🔄. And this is with the basement diffusers closed. What's next step?
Who's the most ignored user on the forums?

Offline notyettaken

  • Dansdeals Gold Elite
  • ***
  • Join Date: Aug 2022
  • Posts: 184
  • Total likes: 228
  • DansDeals.com Hat Tips 2
    • View Profile
  • Location: home
Re: HVAC (heating and AC) question
« Reply #424 on: May 26, 2024, 03:46:09 PM »
My central AC unit covers main floor + basement, however my basement ends up being 4-5° cooler than the main floor, my playroom is so cold that kids turn on the baseboard heat there 🔄. And this is with the basement diffusers closed. What's next step?

Set the fan to on (instead of auto) this will mix the upstairs and basement air and equalize them.
Also make sure there is a return (intake) in the basement .

Offline Alexsei

  • Dansdeals Lifetime Presidential Platinum Elite
  • *********
  • Join Date: Sep 2011
  • Posts: 6296
  • Total likes: 2000
  • DansDeals.com Hat Tips 5
    • View Profile
    • Travel & Kivrei Zadikim
  • Location: Truckistan
  • Programs: COVID-24
Re: HVAC (heating and AC) question
« Reply #425 on: May 26, 2024, 03:48:34 PM »
Set the fan to on (instead of auto) this will mix the upstairs and basement air and equalize them.
Also make sure there is a return (intake) in the basement .
Yes, there's a return in the basement. Will try setting the fan to on
Who's the most ignored user on the forums?

Offline CountValentine

  • Dansdeals Lifetime 10K Presidential Platinum Elite
  • *******
  • Join Date: Mar 2013
  • Posts: 17461
  • Total likes: 8280
  • DansDeals.com Hat Tips -1
  • Gender: Female
    • View Profile
  • Location: Poland - Exiled
  • Programs: DAOTYA, DDF Level 3, 5K Lounge
Re: HVAC (heating and AC) question
« Reply #426 on: May 26, 2024, 05:47:36 PM »
Yes, there's a return in the basement. Will try setting the fan to on
This will help when the AC is off, but it will still be colder.
Only on DDF does 24/6 mean 24/5/half/half
Simone Biles: “I love my black job”

Offline yungermanchik

  • Dansdeals Presidential Platinum Elite
  • ********
  • Join Date: Nov 2018
  • Posts: 2968
  • Total likes: 2390
  • DansDeals.com Hat Tips 2
    • View Profile
  • Location: Previous Signatures: If you chapped hana'ah from a post, like it; You think you know the answers and things are the way they seem.. it just ain't so -The Rebbe from Lublin-
Re: HVAC (heating and AC) question
« Reply #427 on: May 26, 2024, 06:51:44 PM »
And this is with the basement diffusers closed. What's next step?
Try sealing some of them  with these:
https://www.homedepot.com/p/Frost-King-15-x-8-3-Pk-Magnetic-Vent-Covers-MC815/100345609
Small people talk about other people.
Average people talk about things
BIG PEOPLE TALK ABOUT IDEAS.

Offline Alexsei

  • Dansdeals Lifetime Presidential Platinum Elite
  • *********
  • Join Date: Sep 2011
  • Posts: 6296
  • Total likes: 2000
  • DansDeals.com Hat Tips 5
    • View Profile
    • Travel & Kivrei Zadikim
  • Location: Truckistan
  • Programs: COVID-24
Re: HVAC (heating and AC) question
« Reply #428 on: May 26, 2024, 07:29:30 PM »
Who's the most ignored user on the forums?

Offline aygart

  • Dansdeals Lifetime 10K Presidential Platinum Elite
  • *******
  • Join Date: May 2008
  • Posts: 19428
  • Total likes: 15848
  • DansDeals.com Hat Tips 14
    • View Profile
    • Lower Watt Energy Brokers
  • Programs: www.lowerwatt.com
Re: HVAC (heating and AC) question
« Reply #429 on: May 26, 2024, 07:32:50 PM »
Be careful with closing vents since it can cause condensate on the ducts
Feelings don't care about your facts

Offline Alexsei

  • Dansdeals Lifetime Presidential Platinum Elite
  • *********
  • Join Date: Sep 2011
  • Posts: 6296
  • Total likes: 2000
  • DansDeals.com Hat Tips 5
    • View Profile
    • Travel & Kivrei Zadikim
  • Location: Truckistan
  • Programs: COVID-24
Re: HVAC (heating and AC) question
« Reply #430 on: May 26, 2024, 07:55:03 PM »
Be careful with closing vents since it can cause condensate on the ducts
So what's the solution add zoning with dampers?
Who's the most ignored user on the forums?

Offline aygart

  • Dansdeals Lifetime 10K Presidential Platinum Elite
  • *******
  • Join Date: May 2008
  • Posts: 19428
  • Total likes: 15848
  • DansDeals.com Hat Tips 14
    • View Profile
    • Lower Watt Energy Brokers
  • Programs: www.lowerwatt.com
Re: HVAC (heating and AC) question
« Reply #431 on: May 26, 2024, 08:00:22 PM »
So what's the solution add zoning with dampers?
Closing off at the trunk line
Feelings don't care about your facts

Offline Alexsei

  • Dansdeals Lifetime Presidential Platinum Elite
  • *********
  • Join Date: Sep 2011
  • Posts: 6296
  • Total likes: 2000
  • DansDeals.com Hat Tips 5
    • View Profile
    • Travel & Kivrei Zadikim
  • Location: Truckistan
  • Programs: COVID-24
Re: HVAC (heating and AC) question
« Reply #432 on: May 26, 2024, 08:12:35 PM »
Closing off at the trunk line
Permanently? Semi permanently?
Who's the most ignored user on the forums?

Offline aygart

  • Dansdeals Lifetime 10K Presidential Platinum Elite
  • *******
  • Join Date: May 2008
  • Posts: 19428
  • Total likes: 15848
  • DansDeals.com Hat Tips 14
    • View Profile
    • Lower Watt Energy Brokers
  • Programs: www.lowerwatt.com
Re: HVAC (heating and AC) question
« Reply #433 on: May 26, 2024, 08:28:15 PM »
Permanently? Semi permanently?
You can put a manual damper there depending on access
Feelings don't care about your facts

Offline somefield

  • Dansdeals Silver Elite
  • **
  • Join Date: Nov 2013
  • Posts: 98
  • Total likes: 11
  • DansDeals.com Hat Tips 0
    • View Profile
  • Location: Cleveland, Ohio
Re: HVAC (heating and AC) question
« Reply #434 on: May 28, 2024, 09:38:24 AM »
So what's the solution add zoning with dampers?
Arzel Zoning. They have the simplest retrofit branch damper solution.

Offline CountValentine

  • Dansdeals Lifetime 10K Presidential Platinum Elite
  • *******
  • Join Date: Mar 2013
  • Posts: 17461
  • Total likes: 8280
  • DansDeals.com Hat Tips -1
  • Gender: Female
    • View Profile
  • Location: Poland - Exiled
  • Programs: DAOTYA, DDF Level 3, 5K Lounge
Re: HVAC (heating and AC) question
« Reply #435 on: May 28, 2024, 09:54:06 AM »
Arzel Zoning. They have the simplest retrofit branch damper solution.
What is the cost for something like that?
Only on DDF does 24/6 mean 24/5/half/half
Simone Biles: “I love my black job”

Offline somefield

  • Dansdeals Silver Elite
  • **
  • Join Date: Nov 2013
  • Posts: 98
  • Total likes: 11
  • DansDeals.com Hat Tips 0
    • View Profile
  • Location: Cleveland, Ohio
Re: HVAC (heating and AC) question
« Reply #436 on: May 28, 2024, 10:43:16 AM »
What is the cost for something like that?
Hard to say. Each install is custom to that specific home/office (i.e., number of zones & dampers).

Offline CountValentine

  • Dansdeals Lifetime 10K Presidential Platinum Elite
  • *******
  • Join Date: Mar 2013
  • Posts: 17461
  • Total likes: 8280
  • DansDeals.com Hat Tips -1
  • Gender: Female
    • View Profile
  • Location: Poland - Exiled
  • Programs: DAOTYA, DDF Level 3, 5K Lounge
Re: HVAC (heating and AC) question
« Reply #437 on: May 28, 2024, 11:14:18 AM »
Hard to say. Each install is custom to that specific home/office (i.e., number of zones & dampers).
Was just wondering ballpark figures for say a two story, 4-bedroom house. Going to guess it is not cheap.
Only on DDF does 24/6 mean 24/5/half/half
Simone Biles: “I love my black job”

Offline notyettaken

  • Dansdeals Gold Elite
  • ***
  • Join Date: Aug 2022
  • Posts: 184
  • Total likes: 228
  • DansDeals.com Hat Tips 2
    • View Profile
  • Location: home
Re: HVAC (heating and AC) question
« Reply #438 on: May 28, 2024, 03:09:52 PM »
Set the fan to on (instead of auto) this will mix the upstairs and basement air and equalize them.
Also make sure there is a return (intake) in the basement .

@Alexsei did this help?

Offline Alexsei

  • Dansdeals Lifetime Presidential Platinum Elite
  • *********
  • Join Date: Sep 2011
  • Posts: 6296
  • Total likes: 2000
  • DansDeals.com Hat Tips 5
    • View Profile
    • Travel & Kivrei Zadikim
  • Location: Truckistan
  • Programs: COVID-24
Re: HVAC (heating and AC) question
« Reply #439 on: May 28, 2024, 03:10:25 PM »
Who's the most ignored user on the forums?